NUT Troubleshooting Help - No Diagnostics

Started by mintchipmadness, June 24, 2023, 05:05:17 AM

Previous topic - Next topic
Hello,
I have an Eaton 9px1500rt UPS with a network management card (Network-m2). The management card uses the snmp-driver in NUT. Unfortunately I cannot get diagnostics from the UPS in opnsense. I checked the log and I get the error below. I have snmp setup on the UPS with the community name "public". Is there something I am missing? Thank you for your help.


/usr/local/etc/rc.d/nut: WARNING: failed precmd routine for nut

I added an argument with the IP address and port of the management card of the UPS and everything now works

If you don't mind me asking: how did you configure the NUT plugin in OPNSense?

I'm also trying to connect OPNSense to a Eaton UPS with Network-M2 management card but haven't had any luck... the nut logs are saying 'Error   upsmon   Login on UPS [ups-02] failed - got [ERR ACCESS-DENIED]'

Below are the settings of NUT and the UPS itself:



Nvm... right after posting my comment it suddenly started working out of nowhere, I now have working diagnostics  ;D